Host Engineering Forum

General Category => Do-more CPUs and Do-more Designer Software => Topic started by: jwbaker3 on December 13, 2019, 10:05:43 AM

Title: DoMore BRX comm to AB Controllogix with ethernet IP
Post by: jwbaker3 on December 13, 2019, 10:05:43 AM
What is the best way to message data between a BRX and a Controllogix with Ethernet? Both on the same subnet.

Thanks,
JW
Title: Re: DoMore BRX comm to AB Controllogix with ethernet IP
Post by: ATU on December 13, 2019, 10:18:37 AM
Use the Explicit Message Server.
Title: Re: DoMore BRX comm to AB Controllogix with ethernet IP
Post by: jwbaker3 on December 16, 2019, 08:40:42 AM
Thanks for the reply. I already know this, I have used DoMore's to talk to many other pieces of hardware with Ethernet IP but never an AB Controllogix. I am look for an example of how to set up the AB and the DoMore. I tried to get the AB to talk to the BRX but had comm failures. I am sure it is a setup problem.

Thanks,
JW
Title: Re: DoMore BRX comm to AB Controllogix with ethernet IP
Post by: ATU on December 16, 2019, 10:39:58 AM
Attached is a module for setting up the MSG instruction for a CLX
Title: Re: DoMore BRX comm to AB Controllogix with ethernet IP
Post by: jwbaker3 on December 20, 2019, 09:50:21 AM
Thank you for the example, just what I needed. I could not see the forest for the trees..

Thanks again!!!
JW