Ok, so this one also fits in the category of "Idiot Mode" but since my PLCs will be in remote areas that can't easily be reached I need a way to do a full restart including devices - the same as setting the run mode to STOP and then back to RUN. I tried restarting $Main but that doesn't restart the devices. Is such a thing possible?
-
If you monitor places in your program where you could possibly hang (you should do this anyway), you can do soft resets on programs. However, if you desire a hard reset, an old fashion hardware timer that requires a pulse from the PLC periodically or else the timer times-out and opens a NC relay to the main power to the CPU.
-
You could use the REBOOT instruction.
-
You could use the REBOOT instruction.
I issued the REBOOT and it gets stuck in a boot loop. LEDs flash to to bottom as normal followed by all-green, then repeat. Run switch is in RUN position.
Moving the Run switch to STOP and then back to RUN resolves the problem and the PLC completes the bootup sequence.
BX-DM1E-10ER3-D
Do-more : 2.6.0
OS : 2.6.1
Booter : 1.0.6
FPGA : 1.11
Hardware : 6A 3A
-
Did you clear the condition that enabled the REBOOT instruction prior to invoking it?
-
No. The program is a single rung with an ST1 condition and a REBOOT command.
-
Every time the system reboots, it runs the REBOOT instruction again. Rinse, repeat. Don't do that.
-
It's not in $Main. The command gets received by a different program which executes a RUN that starts the program containing the REBOOT.
-
It's not in $Main. The command gets received by a different program which executes a RUN that starts the program containing the REBOOT.
And that program is probably retentive and still running after the restart.
-
And that program is probably retentive and still running after the restart.
Of course you were right. All fixed. Thanks Bob.