in a brx plc working with a pid i am looking for an easy way to set an alarm if the PID_0.PV gets bigger than the
PID_0.SP by some percentage like 5 or 10
-
Calculate the deviation percentage to your SP PV units, then use ALDEV.
-
i wish that the ALDEV would give me an option of deviation percentage not a number because the number for 400 deg would be way different than 1200 deg and if that is not an option any ideas on how the calculation would look.
-
Use a MATH instruction to calculate a variable deviation (Dev). The percentage value should be between 0.0 and 100.0
MATH Dev "(PV * Percentage) / 100.0)"
Then use Dev as the Deviation Limit in your ALDEV:
ALDEV Input:PV Setpoint:SP DeviationLimit:Dev PosAlarm:AlarmA NegAlarm:AlarmB