After updating the BRX OS and Booter I am getting an I/O system warning ($IO Error, ST152). I upgraded the OS from 2.3 to 2.5.2 and the booter from 1.0.4 to 1.0.5. Now I am receiving a warning. Is this due to the OS or the booter? Should I revert back to 1.0.4?
I am running a BRX-DM1E-36ER3-D (no additional expansion cards).
-
Bring up the I/O System View to see what the issue is. On the menu, select PLC->I/O System
Tell us what it says.
-
Wish it said more than this...
-
The I/O System view has a bug that it is currently not providing which channel on the on-board analog input channels is the issue (fix should be out very soon).
Regardless, it is most likely that one (or more) of your on-board WX's is configured for 4-20 mA current, and it is missing its signal. Either wire it up (and getting at least 4mA), or if it's unused, reconfigure it to be voltage (this is the default).
-