DMD is giving me grief about the following code:
// Ver(103) PCU(3) Do-more Designer Clip Source Project: C:\Users\Public\Documents\Do-more\Designer2_3\Projects\~DmD11 Format: Do-more Designer 2.00+ DO-MORE Ladder
PLC BX-DM1-36ER
STRPD T[V0].Done
MATH MHR101 "V0 * LKR_EntrySize"
MATH MHR200 "HMI_AlarmScrnID"
#BEGIN ELEMENT_DOC
"SK","LKR_EntrySize","50",""
"SK","HMI_AlarmScrnID","5",""
#END
I get the error
[Error] $Main#5(@35) E128 Array reference parameter T[V0].Done found within Leading Edge One-Shot Contact within a loop (FOR at $Main@14)
Now I'm running the loop non-yielding (timer works for example), and the location is indexed so any given timer and contact are only seen once per scan, so you'd think one-shots should work. DMD gives me the option to ignore this error for this location. Will it work as expected?
-
Oh, just noticed you can't access Txx.PRE. How hard would it be to add as an accessible member the structure?
-
The preset isn't in the structure, it's only in the instruction. Not hard to do, but a big impact.
The edge isn't going to behave the way you think. If will only be true for the first pass through the loop.
-
The preset isn't in the structure, it's only in the instruction. Not hard to do, but a big impact.
Not a big deal then.
The edge isn't going to behave the way you think. If will only be true for the first pass through the loop.
So even though the reference resolves to a different timer each iteration, the one shot won't track properly?
-
So even though the reference resolves to a different timer each iteration, the one shot won't track properly?
There is a single copy of the previous input state, which is associated with the instruction, not with the input. To do what you are wanting, there would have to be a previous state for every possible input bit in the system. Not practical.
-
There is a single copy of the previous input state, which is associated with the instruction, not with the input. To do what you are wanting, there would have to be a previous state for every possible input bit in the system. Not practical.
I see. I ended up doing this to create a one-shot effect to the timer, which works fine:
// Ver(103) PCU(3) Do-more Designer Clip Source Project: C:\Users\Public\Documents\Do-more\Designer2_3\Projects\Monitor 3 Format: Do-more Designer 2.00+ DO-MORE Ladder
PLC BX-DM1-36ER
FOR V0 AlmRangeStart AlmRangeEnd 1
STR X[V0]
ANDN MC[V0]
STRN X[V0]
AND MC[V0]
ORSTR
TMR T[V0] FaultDebounce
STR T[V0].Done
MATH C0 "(T[V0].Acc - FaultDebounce) < 500"
STR T[V0].Done
AND C0
MATH MHR101 "V0 * LKR_EntrySize"
MATH MHR200 "HMI_AlarmScrnID"
MATH V1 "V0"
#BEGIN ELEMENT_DOC
"SK","AlmRangeStart","4",""
"SK","AlmRangeEnd","39",""
"C0","NewFault","",""
"SK","FaultDebounce","5000",""
"SK","LKR_EntrySize","50",""
"SK","HMI_AlarmScrnID","5",""
#END
-
If you want to use the equivalent of a differential contact in a loop, you will have to do it the old-fashioned way (w/o an edge contact).
Create a block of "previous scan bits", say PSB, the same size as your Timer block. T0.Done previous scan state will be in PSB0, T1.Done will be in PSB1, T255.Done will be in PSB255.
So then your differential behavior inside your FOR/NEXT loop will be
PSB[V0] T[V0].Done
--]/[--------] [------[MATH]
T[V0].Done PSB[V0]
--] [-----------------(OUT)
-
Yup, that's a good approach. In my case, since it was timers I just checked that it was in the first 500ms post-expiration. (Didn't need to be a true single-scan one-shot)