Host Engineering Forum

General Category => Do-more CPUs and Do-more Designer Software => Topic started by: GA Shaffer on January 24, 2018, 05:12:32 PM

Title: Watchdog Timeouts
Post by: GA Shaffer on January 24, 2018, 05:12:32 PM
Hello,
I am experiencing Watchdog Timeouts with increasing frequency. All help appreciated, Thanks!

T1H-DM1E PLC
Modbus FA-ISOCON controlling 8 VFD's
Analog & Digital Inputs
CTRIO
DC Outputs

27 Stage Based Programs

Average Scan Time is 7 ms
Watchdog is set to 1000 ms

PLC does not restart to normal operation.

S3580, Tue Jan 23 09:18:51 2018, PLC rebooted following hardware watchdog timeout.
S3581, Tue Jan 23 09:18:51 2018, System was turned off
S3582, Tue Jan 23 09:18:51 2018, System was turned on

Thanks

Title: Re: Watchdog Timeouts
Post by: plcnut on January 24, 2018, 05:49:10 PM
Are you running the latest firmware?
Title: Re: Watchdog Timeouts
Post by: BobO on January 24, 2018, 10:56:06 PM
VFDs are always tricky. Contact us at support@hosteng.com.
Title: Re: Watchdog Timeouts
Post by: GA Shaffer on January 25, 2018, 03:18:27 PM
Thanks plcnut, Running version 2.1.0 System Info attached