General Category => General Discussion => Topic started by: malcolm58 on June 24, 2008, 06:52:53 PM
-
I am attempting to receive a second ascii string using a data communication module. I have two scales broadcasting an ascii string, The AIN command is working fine on the DL06 port 2. AD tech support said that there is a problem using the AIN with the DO-DCM is there a fix in the works?
-
Host Engineering doesn't make the D0-DCM, Koyo does. There was a minor issue in DirectSOFT 5.2 when configuring the D0-DCM, but that was fixed in 5.3 (free maintenance upgrade that was just released), but that had nothing to do with the actual execution of the AIN instruction.
Do you have any more detail from ADC Tech? If it really is an AIN PLC or D0-DCM firmware issue, they should know the status of the fix.
-
It turns out to be a firmware / Hardware issue on the DCM. The resolution is possibly 4 months out.