I have a rung of code looking to see if DST10 is equal to 3 which turns on a Modbus output coil. However when I place the DM in program mode the Modbus coil remains on. I assume it is because the ladder is no longer running. So how do I read if a DM is in run mode?
-
You can use the $LastScan block to execute code as the PLC is going to program mode.
-
You can also look at a clock bit and see if it keeps toggling.