General Category => DirectSOFT => Topic started by: mhw on July 04, 2017, 09:12:39 AM
-
The SCALEB box in the attached image has "0" in V4500 and is giving an output of 1888 in V4100.What am I doing wrong?
-
Without doing the math, I don't know for certain, but 0 in will be producing a negative result...but V is unsigned.
-
Thanks Bob, I had assumed that the "Out Min" would clamp it at that value. I put in a comparison contact that will clamp it if the "Input" falls below the "In Min".
Have a happy Brexit 1776!
-