I added a line of logic to record blocks of 31 data points on a monthly basis.
(https://forum.hosteng.com/proxy.php?request=http%3A%2F%2Fi.imgur.com%2FXSq1MZp.png&hash=3cde4d9af13afa2a8224c06029f6f77ba0af294e)
When I tried to load this into my PLC, I got this error:
(https://forum.hosteng.com/proxy.php?request=http%3A%2F%2Fi.imgur.com%2FBQTUS6X.png&hash=a48c9392e228687d767677c6872e98d37e319c99)
This is just a DM1E. Is this due to the limit on the RAM size?
-
No. Sounds like we may have a program encode issue. Please send the project to support@hosteng.com and we'll take a look at it. That's a fairly long list of points, I'm betting we have an error in a length limitation somewhere...DmD is allowing something that the controller is disallowing, or something like that.
-
It's most likely a missed error check by the instruction editor. FILELOG editor was missing a few "limit" checks, which SHOULD have been reported as errors when the instruction was edited (e.g. too many entries). We have already fixed a few of these that will be in the next release. I would still like to see the project file, however, or at least that one instruction. Please send it to support@hosteng.com.
Regardless, there is a limit to what a single FILELOG instruction can handle. The work-around is to split it up across 2 (or more) FILELOG instructions with different base file names (e.g. FILELOG w/RunDataA and another FILELOG w/RunDataB).
-
Please send it to support@hosteng.com
Got it! Thanks!
-
The new FILELOG validation check would have caught your situation within the editor. In the next rev, you will get an error message like the attached.