I was watching this video on the AD site <Do-more EtherNet/IP Explicit Client with a Do-more Explicit Server> which showed a Do-More CPU as the (Server) communicating with a Do-More Simulator as the the (Client). So I tried to set things up the other direction - Do-More CPU as the (Client) communicating with the Do-More Simulator as the (Server).
I can't get the comms to work...is it possible to use the simulator as the (Client) communicating with the CPU as the Server or can the Simulator only serve as the client?
-
Should have phrased my Subject as "EIPMSG - CPU to Simulator
-
I believe you can do it. You will have to make sure you open up the correct port(s) in your firewall.
-
Both PLC and simulator support both client and server. EIP server is not enabled by default, so be sure you enable and configure it.
-
Thanks Guys....the Windows Firewall setting did the trick....created a new rule in the advanced settings of Windows firewall to allow the IP address of the Do-More PLC to get through.
Works like a charm.