General Category => CTRIO and CTRIO2 => Topic started by: houleyh on April 04, 2016, 05:46:21 PM
-
Hi, I am working on a drilling application.
The machine will have to go to a certain number of positions and then perform drilling operations. I am working with a Stage programming and DL06.
The whole idea would be to first read the quantity of positions and the position themselves and then cycle the stepper.
Why is this sequence (See Attachment) only working once and stays stuck at the stage 6 because B422.1 (Position loaded) remains OFF?
Thanks for your help
-
I highly recommend you use DirectSOFT's IBoxes for the CTRIO2 to do what you want.
Also, note that [EnableOutput] bit (your B456.0) is something you must turn ON, but [OutputEnable] bit (B422.0) is a bit that is coming from the CTRIO2 telling you that the [EnableOutput] worked. See your Stage S5. That contact should be B422.0 and not B456.0.
Also, I don't know what your Stage S7 is doing because I don't know what you are using V1000 (CTA0) for.
Attached is the PDF with a flowchart for using IBoxes and CTRIO2 for Dynamic Position or Dynamic Position PLUS.
Also, I assume your file #2 in the CTRIO2 is the Dynamic Position profile that you configured.
-
It's a great help, and I want to know if you can point to the source of these content.
-
If you are referring to the PDF flowchart of the CTRIO2, the source of that information is me. I created flowcharts for all the major functions of the CTRIO/CTRIO2. You can download the charts from the CTRIO FAQ0054. To go there, go to our website (hosteng.com), in the left pane, click on FAQs, then select the CTRIO/CTRIO2 as the product, then scroll down to CTRIO FAQ0054.