I have a customer that has a PC setup with 2 network cards. I am logging into the PC with Team Viewer. I can see the PLCs, with NetEdit3 and I can also see them when I try to add a link. I keep getting a time out error? I had them to disable the network card connected to the internet and try to add a link he gets the same time out error. I was onsite last weekend and had no problem connecting to any of them.
Any help would be a big help, I'm not sure what it could be, never had this much trouble. All PLCs are Do-More H2-DM1E, and we are using the unmanaged Stride switches
-
now I'm getting a Error Reading PLC ID?
-
Thanks we got it!
-
Glad you got it worked out.
-
Thanks we got it!
Got what? Was it good? How about telling us the solution in case one of has a similar problem?
-
It ended up being a conflict between the 2 networks cards on the remote PC. The IT guy at the remote site ended up making the card for the PLCs the default card and it worked like a charm.