Host Engineering Forum
General Category => DirectSOFT => Topic started by: ratheret on March 03, 2008, 04:03:32 AM
-
Hi,
Can anybody help me figure out why I can't write my program changes to a Siemens TI335-37 CPU. I have it in 'Program' mode (no switch on this model), Link is established (I can download the program from the PLC for editing), but when I try and save the new code back to the CPU, I get a Memory Write error with the Link Status showing 'No Response from PLC'.
I haven't worked with this model CPU before and have no documentation. Are there links or something else internally on the CPU that need changing?
Thanks,
Dave
-
Thanks anybody who looked at this posting. Problem solved, write protect jumper fitted on board!
-
Great! Thanks for closing it out.