I’m using Ecom 100 cards in various DL PLCs at our treatment plant. It appears that when a DL PLC program is password protected, the ability to write to a bit or boolean is lost. If I connect to the PLC with DS5 using a password or if I remove the password, the ability to write to the bit is restored. V memory locations seem to be unaffected and work ok. I can duplicated the issue using Kepdirect’s OPC server and quick client and with my SCADA software and its Modbus driver.
-
There's a secret handshake! :D
There's some rule for creating a password that still allows comms. IIRC, you have to start the password with an "A" to allow it. If that's not it, it's something like that.
-
Or better answer.....just switch to Do-More! Do-More allows enable/disable of all the various rights for each user class, so this isn't an issue, plus selective protection of individual code blocks.
-
CG, you are correct: The password must start with a capital 'A' to allow write access.