General Category => ECOMs and ECOM100s => Topic started by: keith on November 11, 2014, 04:36:41 PM

Title: ECOM100 throughput with C-More
Post by: keith on November 11, 2014, 04:36:41 PM
I have used ECOMS on numerous jobs for network communications, and I really like the product.  However, we are now using multiple C-More panels communicating with the PLC through the ECOM link, and they really get slow after using about 4 of them.
I realize that the C-More panel is not your product; however, I am using it with your product.

My understanding is that the ECOM can only do 1 transfer per PLC scan, which can be a large block or a single word.

I think the problem is that the panel reads every controls tag without any kind of optimization. 

All of the data I need to communicate between the two devices is in nice small blocks.  It would be nice if the C-More had a way to read a small block of words, then slice them into smaller internal tags to use with the controls (even a single word, then slice it into bits would be ok).  Too bad there is not some kind of generic driver which could read a tag (like a word from the EOM) and break it into smaller internal tags.

I know I can play with the timeout and poll time, but I haven't found a combination which works great.  Too bad the C-More is so wasteful when it comes to bandwidth.

Does anyone have any suggestions ?



Title: Re: ECOM100 throughput with C-More
Post by: franji1 on November 11, 2014, 07:06:15 PM
I know that some people use multiple ECOMs due to a combination of the heavy traffic and needing fast update times.  FYI, depending upon the CPU and frequency and amount of data, an ECOM can get 1 to 4 communication requests per PLC scan.

If you have any extra ECOMs, I would definitely try it before buying just to make sure it works as good as you need.
Title: Re: ECOM100 throughput with C-More
Post by: Controls Guy on November 11, 2014, 07:43:45 PM
For some reason I thought that I remembered that the C-More did in fact optimize.  Maybe I'm thinking of another HMI.  You might also try using a different driver such as Modbus that's supported on both ends of the wire.  One driver might be optimized where the other is not.  Also, I believe it's pretty common in multi-HMI scenarios, to have one HMI be the master and handle all PLC comms, and then serve information to the others, which aren't connected to the PLC.  I know both Idec and Kep (the flowmeter company that makes HMI's, I believe unaffiliated with Kepware) offer this as an option.

If none of that works, I'd suggest looking for an HMI that does optimize it's list.  When I'm writing a driver, I'll even block across small gaps in the list.  Plus the Idec TFT's are IMO far superior to the C-More's.  C-More's have got a lot brighter over the years, but the resolution and color saturation lag far behind the ones used by Idec, and Idec's software is no worse that anyone else's.
Title: Re: ECOM100 throughput with C-More
Post by: ADC Product Engineer on November 12, 2014, 07:43:44 PM
C-more does in fact optimize communications as best it can given the limitations of whatever driver you happen to be using.  ADC has written a white paper on getting the best speed out of your C-more.  You can find it here (http://support.automationdirect.com/docs/an-ea-010.pdf).

Yes I realize that the document says "Screen Update Performance", but screen updates have a direct bearing on how fast communications happens in C-more. 

BTW, 4 screens can be pushing the limit on ECOM performance depending on how much data you are trying to shove through the pipe.  The backplane on a DL205 can only handle about 250 bytes per scan per module.