I need to reset the counter and load a preset table to produce an output on corresponding count values.
Prior to completion of the preset table I need to reset the counter and start the table over.
Do I need to clear the table and reload it when the counter gets cleared?
If I load a table without clearing first will it load over the old one?
-
Do I need to clear the table and reload it when the counter gets cleared?
No. Resetting the counter also resets the table.
If I load a table without clearing first will it load over the old one?
Yes.
-
That's the answer I wanted. I simply want to reset the counter and start the same table again.
Thanks
-
I'm writing my instructions and realize the photo sensors detecting an edge are offset from the datum. I need to set the counter to 750, not zero. That I can do but how do I reset the preset table that's loaded? Load it again or is there a table reset function?
-
The table is reset by the counter being reset. Just use CTREGWR to update the counter with the desired reset value, then reset the counter however you normally do.