Host Engineering Forum

General Category => MB-GATEWAY => Topic started by: Henryp on August 21, 2014, 06:51:39 PM

Title: Future auto detect
Post by: Henryp on August 21, 2014, 06:51:39 PM
Does the Modbus gateway have enough processing power that it could in the future have an auto detect of the serial device(s) it is connected with?
Title: Re: Future auto detect
Post by: rlp122 on August 25, 2014, 12:57:48 PM
How many slaves should it auto-detect?  Should it try every baud, parity, stop bit, etc for each slave?

This would seem to be a pretty slippery slope.  It could literally take hours for the MB-GATEWAY to boot up if it were to auto-detect with no restrictions.
Title: Re: Future auto detect
Post by: Henryp on November 13, 2014, 10:28:20 AM
More like a semi auto detect or how DS5 works on a serial connection. If I try to connect a GS3 and one setting is wrong it won't work. 
Title: Re: Future auto detect
Post by: franji1 on November 13, 2014, 11:11:32 AM
More like a semi auto detect or how DS5 works on a serial connection. If I try to connect a GS3 and one setting is wrong it won't work. 
The DS Auto-Detect for serial ports only tries Address 1.  It cycles baud rates on that one address, not on all 90 possible addresses.  I think Modbus has up to 247 possible addresses?  That would take a LONG time, like rlp122 said.