I only have a question about the Flags section of the help file. It says that SP114 is on when port 2 is in communication. I am using port 2 of the PLC to communicate but, SP116 is the flag I see comming on and off while I communicate through port 2. The program works well but when I use SP116 not SP114. Am I missing something?
-
What CPU (05, 06, 250, 260, 450, etc.)?
-
I just checked - SP116 is the Port 2 "Busy bit" for most CPUs. The 450 "busy bit" for Port 2 is SP114. I'm guessing you are NOT using a 450. We'll update the Help.
-
I'm currently using CPU 06... and thanks for the clarification
-
I'm currently using CPU 06... and thanks for the clarification
Yes, you are correct in your observation that you need to look at SP116 for the "busy bit" for Port 2 on an 06, not SP114. Sorry for the confusion. Help will get some help.