General Category => DirectSOFT => Topic started by: axle_f on January 29, 2008, 03:38:03 PM
-
When is the "overrides" normally available? The 06 manual refers to just setting up bit overrides using the drop down menu. I have not found a way to enable this feature? In the meantime, for testing purposes I have to program a bit around my logic, or change the address to sp1 or sp2 to test the logic.
Any help would be appreciated.
Thanks
-
Your CPU must support overrides (not all CPUs support them, check your PLC manual)
Your DirectSOFT link's protocol must support overrides. K-Sequence supports overrides, but DirectNet does not. Make sure your PLC serial port is configured for K-Sequence and make sure your Link is using K-Sequence. If you are using an Ethernet link, make sure you are using K-Sequence or ECOM protocol (not the ECOM module, but ECOM protocol under the protocol tab).
-
Thank you for the help. This is/was the problem. Do any of the manuals cover this? I could not find it.