General Category => CTRIO and CTRIO2 => Topic started by: jackeroo31 on October 28, 2013, 08:13:35 PM
-
I have a problem that is driving me crazy and I cannot find the solution. I have searched the forums and did not locate an answer.
I have using a CTRIO in slot 4 of a DL06. I am using as an encoder input for axis control.
I have found and understand how to make the counter retentive on power recycle, but I need to preload this counter with a value.
This value will be determined by the operator. What I want to do is press a command button on the HMI will send this this given quota to the CTRIO. I can activate the reset command B3054.1 and it works, but the value resets to '0'. I need to preload this value, then reset the counter to this adjusted value.
I can do this through the CTRIO workbench, but I need to do this at runtime.
I have the CTRIO inputs addressed to V3000 and outputs to V3030.
Any help would be appreciated.
-
See Page 9-9 of the Hx-CTRIO User Manaul (http://www.automationdirect.com/static/manuals/hxctriom/ch9.pdf) over on on the AutomationDirect.com website (http://www.automationdirect.com/adc/Home/Home).
-
That is exactly what I want to do. I found this for Do-more. Ds5 does not have this. Why? I don't know, but it does not.
-
Here is a page from the older manual. Maybe it will help.
-
Sorry, I linked to the wrong chapter. Here is the correct one. (http://www.automationdirect.com/static/manuals/hxctriom/ch8.pdf)
-
Jackeroo31, you must use the WT instruction to write 8 bytes total to the CTRIO's Shared RAM starting at address 80 (hex).
The 8 bytes:
- 1st 2 bytes: 0004 (hex) "Write One Register"
- Next 2 bytes: [RegisterCode]:
0000 = Ch1/Fn1
0001 = Ch1/Fn2
0002 = Ch2/Fn1
0003 = Ch2/Fn2
0004 = Output0
0005 = Output1
0006 = Output2
0007 = Output3
0008 = Ch1/Fn1 Reset
0009 = Ch1/Fn2 Reset
000A = Ch2/Fn1 Reset
000B = Ch2/Fn2 Reset
- Next 4 bytes: [Data], i.e. the count value
So this amounts to something like:
LD K0104 (I think this is correct for Slot4 in DL06)
LD K8
LD K80
WT V4000 (or wherever you store the above 8 bytes)
Then you will Set the Process System Command bit and wait for the System Command Complete bit (for success) or the System Command Error bit (for failure).