If I am in stage 0 of any given program block, and the only instruction is JMP to Stage 1;
Will Stage 1 execute immediately, within the same ladder scan, or on the next ladder scan?
Thanks!
TM
-
if Stage 1 follows Stage 0 in the ladder diagram then the JMP will enable Stage 1 and it will execute on the same scan as the JMP.
If Stage 1 is before Stage 0 in the ladder diagram, the JMP will enable Stage 1, but it will execute on the next scan.
-
Thanks, that's what I needed to know
Another question about scan within a stage:
If I set D10 (for instance) to "1" with a MOVE command in the first rung of a stage,
Will D10=1 for the next rung of the same stage, if I want to compare it?
Thanks again,
TM
-
Yep.
-
Thanks again!
TM