General Category => Do-more CPUs and Do-more Designer Software => Topic started by: Rastus81 on April 22, 2013, 11:51:32 PM
-
Hello All,
Can anyone point me in the right direction with a F2-04THM.
I have a thermocouple connected to CH1, but WX0 is reading 0.
The manual doesn't cover domore plc's.
Thanks
Rastus
-
See if there are any details you need in the Do-more manual
Here's the link to chapter 6:
http://www.automationdirect.com/static/manuals/h2dmm/ch6.pdf
and a link to a page containing links to all the chapters:
http://www.automationdirect.com/pn/doc/manual/h2-dm1e
-
Thanks,
I have that manual. But it only outlines the jumper settings. Im wondering if i need to use any instructions to read the data, like they outline in the module manual.
http://www.automationdirect.com/static/manuals/d2anlg/ch7.pdf
-
I'm not a thermo-couple person, so I don't know how/if the wiring can cause what you are seeing.
-
The short answer is no. If the module is wired correctly and working correctly the data should just show up in WX memory.
-
Double check the wiring, and make sure the PLC is in Run mode. (I don't want to admit how many times I've had problems, and it was because I was in program mode :o )
Also Is the PLC seeing the module in the configuration menu?
-
that module also requires an external 24V connection, make sure it's securely attached, and that the polarity is correct.
-
Thankyou for your replies.
I tried a new thermocouple and the WX register produced a reading.
Although the original thermocouple worked ok in my meter. Maybe i didn't have it secured well enough under the terminal screw.
I wonder if there is an input for open circuit detection?
Thanks again.
Rastus
-
It will be Xn. See page 6-27 of the manual.