I am trying to energize an output on a D2-32TD2 using a D2-260 processor.. the rung is true but the output is not suppying energy to the circuit. The wireing is correct , checked it twice , please help.
-
What is the PLC mode? (Run vs. Stop/Program)?
-
Its in run mode , I think its a I/O config problem , how can I check that??
-
If the I/O config mode is set to 'auto', there isn't much you can do either way. When it powers up, the CPU scans the I/O and configures appropriately.
-
I was wrong on the wiring , if you use a ZL-RT40 feedthrough connector A0 is terminal 21 and A5 is terminal 1 on the connector. After I changed the wiring all was good , what a rookie mistake!!!
-
I was wrong on the wiring , if you use a ZL-RT40 feedthrough connector A0 is terminal 21 and A5 is terminal 1 on the connector. After I changed the wiring all was good , what a rookie mistake!!!
Don't feel bad. I've been doing this for decades and I recently did a similar thing on a job with ZipLinks. I arranged the ZipLinks on a vertical DIN rail with the terminals facing to the right with the first on top, then the second and so on. With the overall flow being from top to bottom, I didn't stop to think till after I wired the first one, that the flow was still left to right within a particular ZipLink, which would be bottom to top in my layout! :D