Author Topic: reading load cell with brx  (Read 602 times)
maciek
Full Member
***
Posts: 46


« on: April 19, 2017, 08:04:29 pm »

what would i use to read a load cell that has 3mv/v output and 10v excitation 
any suggestions
Logged
Controls Guy
Internal Dev
****
Posts: 2358


Darth Ladder


« Reply #1 on: April 19, 2017, 11:02:00 pm »

Signal conditioner.   ADC alone has two series.  Get a 4-20ma output and wire it to the PLC.
Logged

I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.
Evilbeard
Hero Member
*****
Posts: 111


« Reply #2 on: April 21, 2017, 07:23:31 am »

Signal conditioner.   ADC alone has two series.  Get a 4-20ma output and wire it to the PLC.

I like to get the programmable ones, that way I have access to everything I could ever need. (dont' forget the programmer!)

« Last Edit: April 21, 2017, 07:26:12 am by Evilbeard » Logged
maciek
Full Member
***
Posts: 46


« Reply #3 on: April 21, 2017, 06:11:09 pm »

thank you
Logged
maciek
Full Member
***
Posts: 46


« Reply #4 on: April 22, 2017, 10:22:35 pm »

i looked at the specs of that signal conditioner and it doesn't say about millivolts per volt 3mv/v like what the load cell puts out
Logged
b_carlton
Internal Dev
****
Posts: 570



WWW
« Reply #5 on: April 23, 2017, 10:21:06 am »

No, it doesn't appear to be a load cell conditioner. The APD-4051 from API (https://api-usa.com/pdf/api/apd4051.pdf) is similar to what you want though it is incredibly difficult just to find a price. AutomationDirect spoils us.
Logged

An output is a PLC's way of getting its inputs to change.
plcnut
Hero Member
*****
Posts: 710



« Reply #6 on: April 24, 2017, 04:21:32 am »

I am not sure what you are trying to do with a load cell, but it may be wise just to attach the load cell to a scale head and then read the weight from that. This may me necessary for working with scales that must be legal-for-trade. There are also these or these from Futek.
Logged

Circumstances don't determine who we are, they only reveal it.

~Jason Wolthuis
Controls Guy
Internal Dev
****
Posts: 2358


Darth Ladder


« Reply #7 on: April 24, 2017, 12:18:15 pm »

i looked at the specs of that signal conditioner and it doesn't say about millivolts per volt 3mv/v like what the load cell puts out

"mv/v" is not a signal format, it's a hardware characteristic of the load cell.  Feed it 10v, or whatever is within it's range, then take the 0-30mv full scale (or 0-[3 x excitation voltage]mv) and isolate/condition that with the signal conditioner to 0-10v or preferably 4-20ma.

Some thermocouple modules will even handle mv signals (such as from high current DC shunts, etc.) directly, but it's kind of hit and miss how well it works, so I'd stick with the signal conditioner.  IIRC, you're doing this in a BRX, which at this time doesn't have any [local/native] thermocouple inputs anyway.
Logged