Author Topic: Future auto detect  (Read 14583 times)

Henryp

  • Hero Member
  • *****
  • Posts: 161
Future auto detect
« on: August 21, 2014, 06:51:39 PM »
Does the Modbus gateway have enough processing power that it could in the future have an auto detect of the serial device(s) it is connected with?
« Last Edit: August 22, 2014, 10:19:47 AM by Henryp »

rlp122

  • Sr. Member
  • ****
  • Posts: 69
Re: Future auto detect
« Reply #1 on: August 25, 2014, 12:57:48 PM »
How many slaves should it auto-detect?  Should it try every baud, parity, stop bit, etc for each slave?

This would seem to be a pretty slippery slope.  It could literally take hours for the MB-GATEWAY to boot up if it were to auto-detect with no restrictions.

Henryp

  • Hero Member
  • *****
  • Posts: 161
Re: Future auto detect
« Reply #2 on: November 13, 2014, 10:28:20 AM »
More like a semi auto detect or how DS5 works on a serial connection. If I try to connect a GS3 and one setting is wrong it won't work. 

franji1

  • Bit Weenie
  • Host Moderator
  • Hero Member
  • *****
  • Posts: 3658
    • Host Engineering
Re: Future auto detect
« Reply #3 on: November 13, 2014, 11:11:32 AM »
More like a semi auto detect or how DS5 works on a serial connection. If I try to connect a GS3 and one setting is wrong it won't work. 
The DS Auto-Detect for serial ports only tries Address 1.  It cycles baud rates on that one address, not on all 90 possible addresses.  I think Modbus has up to 247 possible addresses?  That would take a LONG time, like rlp122 said.