Host Engineering Forum
 
*
Welcome, Guest. Please login or register.
Did you miss your activation email?
January 19, 2018, 08:04:03 am


Login with username, password and session length


Pages: [1]
  Print  
Author Topic: DNLoader doesn't configure PORT2 on DL05  (Read 21878 times)
hirzel
Newbie
*
Posts: 8


« on: July 29, 2013, 03:01:34 pm »

I've used DNLoader to load programs into DL05's.  Part of my program, I send data out PORT2.

I write a custom windows based companion program that captures the serial data streaming out PORT2, and displays and monitors the PLC INs and OUTs.

I need to set PORT2 to serial communication,  9600 baud, 8 bits, 1 stop, no parity, no handshake.


The problem is,  DLoader doesn't set up the port, so I need to do it with Direct Logic,  which defeats the entire purpose of use DNLoader.

Is there any way to get DNloader to read/write PORT2 setup configuration?

John Mc
Logged
franji1
Bit Weenie
Host Moderator
*****
Posts: 2228



WWW
« Reply #1 on: July 29, 2013, 03:47:53 pm »

You can write ladder logic to configure Port 2.  There is an app note on ADC's website that describes the data values and System V registers, along with a link to a ladder logic example for a 450.  Note that the 05 will be different addresses/values than this example, but by comparing the 450 data/registers against the 05 data/registers, you can figure out the necessary 05 logic to stick in your program.

http://support.automationdirect.com/docs/comportsetup/
Logged

hirzel
Newbie
*
Posts: 8


« Reply #2 on: July 29, 2013, 06:13:46 pm »

Thanks,  I'll give that a shot.

John
Logged
Pages: [1]
  Print  
 
Jump to:  

Powered by MySQL Powered by PHP Powered by SMF 1.1.21 | SMF © 2015, Simple Machines

Valid XHTML 1.0! Valid CSS! Dilber MC Theme by HarzeM