There is a problem if you're logged into the processor and under some conditions if you don't log out but disconnect, the processor will no longer communicate.
rswolff, I believe you are referring to the
"Unable to lock processor" error. This particular issue is not related to your H0-ECOM100 issue. We don't know about that one, but since it is unrelated...
Based on your installation description, it doesn't sound like a noise issue. But, regarding your communication matrix, I have done some research on your problem (based on the database at Automation Direct) and your posts here and I think I gather the following summary. Please tell me if this is correct as there are some things I'm not clear about that I'll indicate with (?).
SUMMARY:
- PLCs 1-6 read 2 bytes from each other every (?) seconds using peer-to-peer ECRXs.
- PLCs 7-10 read 128 bytes from PLCs 1-6 every 2-3 seconds using peer-to-peer ECRXs.
- WonderWare station reads (?) bytes from PLC7 every (?) seconds using KepDIRECT DL-driver.
- WonderWare station reads (?) bytes from PLCs 1-6 only incidentally using KepDIRECT DL-driver.
- Cmores 1-4 read (?) bytes from PLCs (?) every (?) seconds using native DL-driver.
- OP420s 1-6 read (?) bytes from PLCs 1-6 respectively every (?) seconds using PLC serial port (K-seq or DirectNET).
QUESTIONS:
(1) Can you fill out the (?) in the above summary and make any corrections?
(2) Can you tell me what the following H0-ECOM100 Advanced Settings are set to for each of the 10 H0-ECOM100s?
- RX/WX Settings: ACK Timeout
- RX/WX Settings: Resp. Timeout
- RX/WX Settings: Retries
(3) Does this timeout issue happen just at random (over a period of time) or exclusively when you do, say, an online edit?
P.S. I tried calling your phone number and just got a FAX. I tried to speak FAX, but I couldn't understand it.