There are IBox instructions that can read the following pieces of information out of an ECOM100 at runtime and stick it in V memory, then accessible via an HMI:
ECRDIP (IB-722) ECOM100 Read IP Address
ECRDMID (IB-720) ECOM100 Read Module ID
ECRDNAM (IB-724) ECOM100 Read Module Name
ECRDDES (IB-726) ECOM100 Read Module Description
ECRDSNM (IB-732) ECOM100 Read Subnet Mask
ECRDGWA (IB-730) ECOM100 Read Gateway Address
I should have also mentioned that with DirectSOFT Communication Links, you can choose TCP/IP as the Protocol, but then use Module ID or Module Name as the "address". You then must ensure that the Module ID or Module Name is UNIQUE across all PLCs. Note that the Module ID is settable via a "soft" setting (NetEdit) or "hard" setting, via dipswitches on the ECOM100 module. If the lower 6? 7? dipswitches are all "0", then it uses the "soft" ID. If any of those lower 6/7? dipswitches are "1", then it uses that set of dipswitch values as its "hard" ID. So if switch 0 and 1 are ON, then it has a hard ID of 3.