Author Topic: H4-CTRIO configuration problems  (Read 579 times)
Davecassano
Newbie
*
Posts: 1


« on: October 29, 2010, 06:41:07 pm »

Hello. First time trying to configure an H4-CTRIO Module. Trying to use the CTRIO workbench but it never sees the counter module in the PLC rack. When I select the PLC the "Link Active" box is checked but nothing ever shows up. Any ideas on what I am doing wrong? The only boxes available to me are "Clear Config" and "Quit".

Thank you for any help,
David
Logged
MikeS
Host Moderator
*****
Posts: 176



WWW
« Reply #1 on: November 01, 2010, 08:37:10 am »

first thing is to make sure the link you setup is configured to use K-Sequence protocol.

also make sure there are no bent pins on the backplane connector.
Logged