Yes, it is doable. The DL260 in concert with an H2-ECOM100 module can do Modbus TCP either as a client (master) or server (slave). The Modbus function codes supported are shown here:
http://www.hosteng.com/FAQFiles/ECOM.htm#FAQ0038Yes you can use the IBoxes, ECOM100, ECRX and ECWX with the proper addresses in them to generate the desired Modbus function code. Basic steps are:
1. Use NetEdit to configure your H2-ECOM100 with a peer-to-peer entry with Modbus TCP selected as the protocol.
2. Program an ECOM100 IBox at the top of your ladders.
3. Program an ECRX (or ECWX) with the proper addresses to generate the desired Modbus function code. (Use the PDF file in the above FAQ for a quick reference).
Of course, you may need to consult the DL260 and/or ECOM100 manuals for more details; or, ask more questions here to gain a better understanding of the details of the steps above.
Hope this helps!