Quote from: WRT on May 12, 2010, 04:24:16 pm
Glad you noticed that Darth. I rather hoped someone would notice my wit
LBL K666
GOTO K666
PLC Program of the Beast
Logged
I retract my earlier statement that half of all politicians are crooks. Half of all politicians are NOT crooks. There.
WRT
Full Member
Posts: 25
Re: DL06 locking up
«
Reply #16 on:
May 12, 2010, 08:00:33 pm »
This is more fun than Facebook!
Logged
b_carlton
Internal Dev
Posts: 388
Re: DL06 locking up
«
Reply #17 on:
May 12, 2010, 09:11:43 pm »
'Farmville' on a PLC?
Logged
An output is a PLC's way of getting its inputs to change.
WRT
Full Member
Posts: 25
Re: DL06 locking up
«
Reply #18 on:
May 13, 2010, 09:35:32 pm »
I finally found the lock out problem after a week of remote troubleshooting. A Solid State relay "coil" connected to one of the PLC outputs was shorted. I thought I was clever putting in a 1 amp power supply so that all the circuits were protected, but what happened is that the low voltage from the short killed the PLC and left it in a bad state. No wonder it was not communicating! I couldn't forensic it because the PLC wasn't talking every time it tried to turn that output on!
So another moral:
Put a power supply in that is hefty enough to open a separate fuse on the output circuits without dropping the voltage so much that the PLC goes down. Even better, annunciate the fuse so you know what the problem is.
Logged
Controls Guy
Internal Dev
Posts: 1134
Darth Ladder
Re: DL06 locking up
«
Reply #19 on:
May 27, 2010, 02:15:22 pm »
I agree. I usually have a dedicated fuse or breaker on the output common. When you send your kids (wires) out in the world, you never know what's going to happen to them.
Logged
I retract my earlier statement that half of all politicians are crooks. Half of all politicians are NOT crooks. There.
Pages:
1
[
2
]
Print
« previous
next »
Jump to:
Please select a destination:
-----------------------------
General Category
-----------------------------
=> MX Technology Preview
=> General Discussion
=> CTRIO
=> DirectSOFT
=> DNLoader
=> DSData
=> EBCs and EBC100s
=> ECOMs and ECOM100s
=> EDRV
=> ERM
=> Ethernet SDK
=> MB-GATEWAY
=> NetEdit
=> Profibus
=> WinPLC
Loading...