Host Engineering Forum
 
*
Welcome, Guest. Please login or register.
Did you miss your activation email?
February 07, 2012, 09:23:53 am


Login with username, password and session length


Pages: [1]
  Print  
Author Topic: thermopcouple f4-08-thm-n  (Read 883 times)
Harvey
Newbie
*
Posts: 7



« on: March 16, 2010, 09:23:33 am »

New to direct soft.  I need to drive the input high if there a thermocouple is disconnected or shorted. any ideas
Logged
Gene Bond
Newbie
*
Posts: 4


« Reply #1 on: March 16, 2010, 08:30:19 pm »

Forgive me, but I've not used this card, but couldn't you do do a couple of compares that are out of your normal range for alarms? Seemsif the T/C is shorted, the register would read very low, surely lower than normal for the process, and if it's open, it should read very high...

Again, maybe not applicable, but it may help.
Logged
b_carlton
Internal Dev
****
Posts: 370



WWW
« Reply #2 on: March 16, 2010, 10:10:31 pm »

The manual defines that there are "Broken Transmitter Bits".

As far as 'shorted', Gene's suggestion to test against any possible normal measurement is a good one. Be aware though that a shorted thermocouple - the two leads shorted together at some place other than the normal measuring end - will measure the ambient temperature at the shorted point.
Logged

An output is a PLC's way of getting its inputs to change.
Harvey
Newbie
*
Posts: 7



« Reply #3 on: March 17, 2010, 07:56:35 am »

Open it is reading low, if I unwire the t/c it will read 92 deg what I would like this be a read high so the heater does not keep trying to heat.  Other plc cards I have used have a way to configure this; I have not worked much with direct soft.
Logged
b_carlton
Internal Dev
****
Posts: 370



WWW
« Reply #4 on: March 17, 2010, 08:49:37 am »

I repeat:

Quote
The manual defines that there are "Broken Transmitter Bits".

It's not a function of Directsoft. It's a function of the thermocouple card. Read the instructions carefuilly.

Logged

An output is a PLC's way of getting its inputs to change.
Harvey
Newbie
*
Posts: 7



« Reply #5 on: July 31, 2010, 01:43:57 pm »

 yes it is "Broken Transmitter Bits"in on the f4-08thm not the -n. On the f4-08thm-j card it is to go high same as burned out thermocouple this is staying at 95 deg when the termocouple is unplugged. 
Logged
Controls Guy
Internal Dev
****
Posts: 1105


Darth Ladder


« Reply #6 on: July 31, 2010, 01:53:05 pm »

There is no F4-08THM-N listed as a part number on the website.
Logged

I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.
b_carlton
Internal Dev
****
Posts: 370



WWW
« Reply #7 on: July 31, 2010, 02:37:16 pm »

The 'F4-08THM-N' is a shorthand for either of the older cards F4-08THM-J or F4-08THM-K which were single single type thermocouple specific. The (I believe) newer F4-08THM accepts a variety of thermocouples.
Logged

An output is a PLC's way of getting its inputs to change.
Controls Guy
Internal Dev
****
Posts: 1105


Darth Ladder


« Reply #8 on: July 31, 2010, 04:11:24 pm »

Oh, sorry, I assumed it was a module specific to Type N thermocouples analogous to the J and K-type cards.
Logged

I retract my earlier statement that half of all politicians are crooks.  Half of all politicians are NOT crooks.  There.
Harvey
Newbie
*
Posts: 7



« Reply #9 on: August 02, 2010, 09:22:36 am »

My understanding is with the F4-08THM card you can set up each channel for a different type of thermocouple with a jumper, thank you for all the help and input.   Cheesy 
Logged