I have a DL260 processor and I am trying to communicate (H2-ECOM-100) with an Altivar 31 via modbus(RTU) RS485. I have a Connexium TSXETG100 ethernet gateway that I am using to convert the ethernet comms to the RS485 modbus. I cannot seem to get the commands through to the inverter.

Can anyone offer any advice or sample programs that might explain how to do this?

Thanks.
Logged
Greg
HOS†ech
Host Moderator
*****
Posts: 320


Hmmm...


WWW
« Reply #1 on: May 15, 2009, 04:17:54 pm »

The H2-ECOM100 has to be configured using NetEdit (free software). The H2-ECOM100 has to have a Peer-to-peer table in it that points to the Connexium TSXETG100 ethernet gateway's IP address. Then you use the RX/WX (or IBox ECRX/ECWX) instructions in the DL260 to read and write.

Also, the H2-ECOM100 does true Modbus TCP, not Modbus RTU on TCP.