News:

  • June 10, 2026, 07:08:02 PM

Login with username, password and session length

Author Topic: Ramp Soak ramp slope counts per second  (Read 51033 times)

rlawson

  • Newbie
  • *
  • Posts: 4
Ramp Soak ramp slope counts per second
« on: May 15, 2007, 06:17:02 AM »
I have a heat treating process where I want to use the ramp soak generator with a 260 cpu system. The problem that I have is the ramping counts per second function. For example I need to ramp at a rate of 100 deg F per hour. With the ramp slope variable I am limited from 00.00 to 99.99 counts per second. 100 deg per hour equates to .0277. .01 gives me 36 deg F per hour, .02 gives 72 deg/hr, and .03 gives 108. Since I need to maintain 100 degrees instead of 72 or 108, what are my options? Is this beyone the capabitity of the built in ramp soak generator?
Tks, Robert

MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 264
    • Host Engineering, Inc.
Re: Ramp Soak ramp slope counts per second
« Reply #1 on: May 23, 2007, 03:34:26 PM »
That's all you have to work with in these PLCs.

You'll have to roll your own ramp/soak table in your ladder code to get the steps you need.
Good design costs a lot. Bad design costs even more.

rlawson

  • Newbie
  • *
  • Posts: 4
Re: Ramp Soak ramp slope counts per second
« Reply #2 on: June 08, 2007, 06:40:05 AM »
Thats what I figured, thanks for confirming what I suspected.

Robert

BobO

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 6158
  • Yes Pinky, Do-more will control the world!
Re: Ramp Soak ramp slope counts per second
« Reply #3 on: June 09, 2007, 12:45:03 PM »
Sound like a good feature for a future PLC...ramp/soak generator with selectable time base... ;)
"It has recently come to our attention that users spend 95% of their time using 5% of the available features. That might be relevant." -BobO