Hi,
I have been using Directsoft PLC`s for sometime now (DL05`s and 06`s), and recently I had a problem with a DL06-DD1 being used in a control panel for an injector machine. After connecting and powering up the system, with progam downloaded and I/O wired to it, it happened that while making some changes on the fly, after the 3rd or 4th Run Mode download, it faulted, showing the red LED on the PLC. After powering off/powering back on, the Fault LED was off but I was never able to communicate with this PLC again. I am using a GS2 inverter located in the same panel, aprox 10 inches away from the PLC. After testing during a time, the Fault LED turned on again. My 2 questions basically are: 1) Is it possible that an error in the program could lead to this unrecoverable fault condition on the PLC? I was using some GOTO instructions, and thinking that perhaps the program jumped out to some unprogrammed or bad memory location, I decided to take out this instruction from the program. I replaced the PLC with another of the same model, and has been working fine ever since. Question 2) Is it possible that the inverter`s operation frequency could be corrupting the memory in the PLC? I am planning to add Line reactors to the GS2 at input and output, EMI and RF filtering, but this will help the inverter not the PLC.
Thanks in advance. Your valuable input will help me design panel component location layout in a better way and also understand if the issue could be caused or not by the way it is programmed.
-EZ