News:

  • June 12, 2026, 02:08:22 PM

Login with username, password and session length

Author Topic: ASI Master / Scanner?  (Read 19023 times)

sgsims

  • Hero Member
  • *****
  • Posts: 127
ASI Master / Scanner?
« on: January 10, 2008, 10:40:38 AM »
Any plans to introduce an ASI Master/Scanner that fits into the DL205 backplane? 

The only way I can see to use an ASI network now is to use an ASI master/Modbus gateway in conjunction with an ECOM card.  Because the ECOM card requires the RX / WX instrctions to come from the ladder logic I think the I/O update would too slow.


MikeS

  • Host Moderator
  • Hero Member
  • *****
  • Posts: 264
    • Host Engineering, Inc.
Re: ASI Master / Scanner?
« Reply #1 on: January 11, 2008, 09:51:27 AM »
we don't have any current plans for buliding one of these. and you're correct that using an asi-gateway and an ecom100 -for modbus rcp/ip communication - would work, but the update rate is tied to the plc scan.

definitely contact automationdirect.com and make your request known to them. we get a majority of our engineering direction from them, so if enough folks them ask fo rit, they'll ask us to build it. we're very capitalist that way.  ;)
Good design costs a lot. Bad design costs even more.