I have a DL06 set up as a Modbus TCP Master to communicate to 7 Modbus Slaves. The all communicate fine. The problem is that I can't connect with Direct Soft. If I cycle the power to the 06 it will work for a while until the ECOM100 receives a timeout error then strange things happen. To work around that problem I installed another ecomm to connect to the 06 with direct soft. I have version 5.2. This seem to be a problem with the ECOMM100, otherwise everthing work OK. I would like to know if that is problem, or what else I could try? I can't understand what is happening because I can see the ECOMM in netedit but can't make a link to it.
|
|
|
|
|
Logged
|
|
|
|
|
ATU
|
 |
« Reply #1 on: November 13, 2007, 06:22:30 pm » |
|
How often are you polling the slaves? I am not sure what the priorities are in servicing the requests from Directsoft, but could it be possible that the polling rate is so high that the module never has time to link with Directsoft? I know there has to be some sort of limit. You did say that adding a second ECOM modules allowed you to link up.
|
|
|
|
|
Logged
|
|
|
|
amos
Newbie

Posts: 9
|
 |
« Reply #2 on: November 13, 2007, 07:03:07 pm » |
|
I only use the other ecom to connect with direct soft. I use the ibox instruction driven by sp1. It polls all the nodes in about half a second.
|
|
|
|
|
Logged
|
|
|
|
|
ATU
|
 |
« Reply #3 on: November 13, 2007, 07:11:10 pm » |
|
Do you have any delay between polls or do you poll consectively through the slaves 1-6 and then back to 1 without any delay?
|
|
|
|
|
Logged
|
|
|
|
Greg
HOS†ech
Host Moderator
    
Posts: 320
Hmmm...
|
 |
« Reply #4 on: November 14, 2007, 10:11:21 am » |
|
Since you can see the module in NetEdit, this just means that the Ethernet side of things is working. I also venture to say since your Modbus TCP communications is continuing to work that the PLC side of things is also working.
Some questions: (1) Your question revolves around using just 1 H0-ECOM100 for the Modbus TCP mastering and connection to DirectSOFT, right? (2) Does installing the 2nd H0-ECOM100 for a dedicated DirectSOFT link fix all the issues? (3) In NetEdit, does the CPU Test pass for the 1st H0-ECOM100? (4) What error do you get in DirectSOFT when you try to make a link to the 1st H0-ECOM100?
It also may be interesting to find out exactly what is going on on the network as a whole by using Wireshark (free Ethernet sniffer) to log a sample of the telegrams when you are trying to make a link. Of course, this would require a hub (not a switch) for the sampling.
|
|
|
|
|
Logged
|
"You have to believe in free will. You have no choice." -Isaac Bashevis-Singer
|
|
|
amos
Newbie

Posts: 9
|
 |
« Reply #5 on: November 14, 2007, 10:56:01 pm » |
|
"Do you have any delay between polls or do you poll consectively through the slaves 1-6 and then back to 1 without any delay?" Yes that would be the case.
(1) Your question revolves around using just 1 H0-ECOM100 for the Modbus TCP mastering and connection to DirectSOFT, right? Yes I am wondering what is happening. If the link is comunicating without any errors than I could conect with DirectSoft until there are a few timeout errors, after that I cant make a link anymore.
(2) Does installing the 2nd H0-ECOM100 for a dedicated DirectSOFT link fix all the issues? Yes it does almost. The only problem was I couldn't conect to the PLC.
(3) In NetEdit, does the CPU Test pass for the 1st H0-ECOM100? Yes (4) What error do you get in DirectSOFT when you try to make a link to the 1st H0-ECOM100? I'm not at the PLC now so I can't answer. When i tried to make a new link I got as far as selecting the ECOM module.
|
|
|
|
|
Logged
|
|
|
|
|
ATU
|
 |
« Reply #6 on: November 15, 2007, 01:16:52 am » |
|
Just for an experiment if your application requirement allows this, try adding a delay at the point in time that you finish communicating with Slave 6 and before polling Slave 1. Start at 500ms and see if you can link up. If so, back it off from there and see how small you can make the delay without having a link timeout. Use a fast timer. If it works, you may want to try adding a shorter delay between every poll, rather than one longer delay.
|
|
|
|
|
Logged
|
|
|
|
|
MikeS
|
 |
« Reply #7 on: November 15, 2007, 11:49:24 am » |
|
what i suspect is going wrong is that you're getting errors & retrys in the modbus communications that are hogging the tcp/ip stack, which is causing some problems when the directsoft comm comes around.
you said the modbus comm portion of your program is essentially an sp1 contact and the netwx iboxes. is your program looking at the individual success and error bits from the netwx iboxes?
the way i've done these polling programs using iboxes is: do the first ibox wait on success or error to come on if error - increment ibox_1_error_cnt ( optionally stop here or enable next ibox ) if success - increment ibox_1_ok_cnt & enable next ibox -- repeat for each node -- last ibox success enables first ibox again
this chaining method makes sure each node's activity (good or bad) is reported
this method also has the advantage of giving you a convenient place to insert some delay timers if needed
|
|
|
|
|
Logged
|
Good design costs a lot. Bad design costs even more.
|
|
|
amos
Newbie

Posts: 9
|
 |
« Reply #8 on: November 16, 2007, 07:39:47 pm » |
|
you said the modbus comm portion of your program is essentially an sp1 contact and the netwx iboxes. is your program looking at the individual success and error bits from the netwx iboxes? Yes I have a counter for both error and success. In 48 hours I got on some nodes at the most 2 errors some had none.
the way i've done these polling programs using iboxes is: do the first ibox wait on success or error to come on if error - increment ibox_1_error_cnt ( optionally stop here or enable next ibox ) if success - increment ibox_1_ok_cnt & enable next ibox -- repeat for each node -- last ibox success enables first ibox again
this chaining method makes sure each node's activity (good or bad) is reported I tried your suggestion and it works. I can still make a link after a few timeouts. I taught the IBox instruction is supposed to take care or the enable bits?
this method also has the advantage of giving you a convenient place to insert some delay timers if needed Didn't bother with the timers it works fine without them.
Thanks Everybody for the help. Amos
|
|
|
|
|
Logged
|
|
|
|
amos
Newbie

Posts: 9
|
 |
« Reply #9 on: November 17, 2007, 10:59:49 am » |
|
It looks like I posted to soon it still does the same thing. Also installed some timers at the last IBox with a 1 second delay it still doesn't work. It's OK it works when using the other Ecom to connect.
|
|
|
|
|
Logged
|
|
|
|
|
ATU
|
 |
« Reply #10 on: November 18, 2007, 11:52:23 pm » |
|
You say that you made the changes and it worked then it doesn't work. Can you give more information of what happened? Were you able to connect? Can you post the part of the program that you are doing the polling? What brand of Network Switch are you using?
|
|
|
|
|
Logged
|
|
|
|
|
franji1
|
 |
« Reply #11 on: November 19, 2007, 11:13:07 am » |
|
Make sure you have the most recent firwmare. Run NetEdit3 and click on File->Live Update to get the latest and greatest firmware, then upgrade your ECOM100 module if needed.
|
|
|
|
|
Logged
|
|
|
|
amos
Newbie

Posts: 9
|
 |
« Reply #12 on: November 20, 2007, 04:14:59 pm » |
|
You say that you made the changes and it worked then it doesn't work. Can you give more information of what happened? Were you able to connect? No It says Error connecting to PLC! Error: Ext Error: Can you post the part of the program that you are doing the polling?
This is the code. PLC 06
// Rung 1 // Address 0 ECOM100 K0 K4 V1400 V1401 V1402
// Rung 107 // Address 1504 STR C1000 ECWX K0 V510 K21 VC300 K1 C0 C400 C401
// Rung 108 // Address 1610 STR C400 INC V400
// Rung 109 // Address 1613 STR C401 INC V401
// Rung 110 // Address 1616 STR C400 OR C401 RST C1000 SET C1001
// Rung 111 // Address 1620 STR C1001 ECWX K0 V511 K29 VC320 K1 GY20 C402 C403
// Rung 112 // Address 1726 STR C402 INC V402
// Rung 113 // Address 1729 STR C403 INC V403
// Rung 114 // Address 1732 STR C402 OR C403 RST C1001 SET C1002
// Rung 115 // Address 1736 STR C1002 ECRX K0 V512 K2 V5670 K32 V4000 C404 C405
// Rung 116 // Address 1842 STR C404 INC V404
// Rung 117 // Address 1845 STR C405 INC V405
// Rung 118 // Address 1848 STR C404 OR C405 RST C1002 SET C1003
// Rung 119 // Address 1852 STR C1003 ECWX K0 V513 K3 VC40 K1 GY20 C406 C407
// Rung 120 // Address 1958 STR C406 INC V406
// Rung 121 // Address 1961 STR C407 INC V407
// Rung 122 // Address 1964 STR C406 OR C407 RST C1003 SET C1004
// Rung 123 // Address 1968 STR C1004 ECRX K0 V514 K4 TA0 K16 V4100 C410 C411
// Rung 124 // Address 2074 STR C410 INC V410
// Rung 125 // Address 2077 STR C411 INC V411
// Rung 126 // Address 2080 STR C410 OR C411 RST C1004 SET C1005
// Rung 127 // Address 2084 STR C1005 ECRX K0 V515 K5 V2400 K16 V4200 C412 C413
// Rung 128 // Address 2190 STR C412 INC V412
// Rung 129 // Address 2193 STR C413 INC V413
// Rung 130 // Address 2196 STR C412 OR C413 RST C1005 SET C1006
// Rung 131 // Address 2200 STR C1006 ECRX K0 V516 K6 V6033 K16 V4300 C414 C415
// Rung 132 // Address 2306 STR C414 INC V414
// Rung 133 // Address 2309 STR C415 INC V415
// Rung 134 // Address 2312 STR C414 OR C415 RST C1006 OUT C1007
// Rung 135 // Address 2316 STR C1007 ECWX K0 V517 K7 VC60 K1 GY20 C416 C417
// Rung 136 // Address 2422 STR C416 INC V416
// Rung 137 // Address 2425 STR C417 INC V417
// Rung 138 // Address 2428 STR C416 OR C417 RST C1007 SET C1010
// Rung 139 // Address 2432 STR C1010 ECRX K0 V520 K8 TA0 K16 V4400 C420 C421
// Rung 140 // Address 2538 STR C420 INC V420
// Rung 141 // Address 2541 STR C421 INC V421
// Rung 142 // Address 2544 STR C420 OR C421 RST C1010 SET C1011
// Rung 143 // Address 2548 STR C1011 TMR T30 K10
// Rung 144 // Address 2552 STR T30 RST C1011 SET C1000
// Rung 145 // Address 2555 STR SP1 RST C400 C421
Another Question Where could I find information on the timeout settings for Modbus TCP. I have looked in the manual and can't find anything. Also slave timeout what is that for? Factory default is 20 sec. Thanks Amos
|
|
|
|
|
Logged
|
|
|
|
|
ATU
|
 |
« Reply #13 on: November 20, 2007, 04:45:49 pm » |
|
The only thing that I can see that may be a problem (I'm not really sure if it is) is that you could have 2 WX boxes active on the same scan or at a minimum 1 WX active on all scans. When 1 completes the next one is activated but not really allowed to be scanned in the inactive state. The effect would be that you are never at the bottom of the program when the ECOM module is not being called to do something. Try reversing the program flow. Start polling at the bottom of the program and work you way up. That way when a WX instruction is completed, the ladder ends with no active WX instruction until the next scan.
|
|
|
|
|
Logged
|
|
|
|
jsatkanpak
Newbie

Posts: 8
|
 |
« Reply #14 on: January 11, 2008, 07:04:39 pm » |
|
We've found that in high-traffic situations there is definitely a "sweet spot" for polling speed. Too fast and the communications breaks down -- too slow and the update rate is unacceptable. We started using a 100ms polling rate and have had excellent results. We use Modbus/TCP-to-DeviceNet a lot through AnyBus protocol converters and it's been a great solution.
|
|
|
|
|
Logged
|
|
|
|
|